I need to move my sprinkler controller, and don't have enough wire to move it. But I DO have some solid strand Cat 5 cable, can I use that instead? Moving it about 30 feet.
 

frieed

Jeepless in Draper
Supporting Member
Location
Draper, UT
Sprinkler wire is typically about 16ga while cat 5 is usually 24ga
It "may" work, but you may also get too much voltage drop to actuate the solenoid.
 

phatfoto

Giver of bad advice
Location
Tooele
Darned good point. I've complained since I bought this house, the PO put in the front and rear sprinkler stations in the basement. Very difficult to run them and check the yard when running in and out of the house. So I'm moving the front station to the garage. And there is plenty of wire to move the rear station up into the kitchen cabinets. Reckon I'll go and get what I need later today.
 